Hi all
Has anybody used IDEAL SURETEST Circuit Tracer equipment. IT costs around 300 - 350 pounds when i saw it at exhibition at Sandown Park, in December.
Has anybody had success fault finding with this equipment?
Would it find open circuits when doing ring main continuity, because i had to open a number of sockets to find disconnected neutral then a earth at the weekend.
I guess this can be used for PIRs.
I saw a article in the Professional Electrican monthly magazine on this and was rated highly by one company.
thanks
Admin1
Forum Founder
Feb 6, 2008
10,229
-1
I have looked - But failed so far,sorry Mate.
I will keep trying. :)
steptoe
Feb 13, 2008
24,422
160
Gtr Manchester
have used loadsa gear similar to that buddy, but a helluva lot cheaper.
basically it measures the length of the circuit, either open or close, so will tell you how far away the fault is.
absolutely rubbish at helping you locate a fault if its wired all higgle de piggle de,
as is usual with older houses, or the ones the fault is always in.
they are derived from telecoms and underground fault finders where the cable is pretty obvious in its run.
ps, never actually used the one you asked about so if im totally wrong in summising how it works Im really sorry.
steptoe
Feb 13, 2008
24,422
160
Gtr Manchester
Hi allHas anybody used IDEAL SURETEST Circuit Tracer equipment. IT costs around 300 - 350 pounds when i saw it at exhibition at Sandown Park, in December.
thanks
ps, quick way to find 1 broken conductor in a ring is simply to lift that leg out of the MCB/N bar/E bar and power up, then check each socket with your ELI plug.
Apr 13, 2008
70
Hi Steptoe,
is this what you mean for finding break in ring conductor:
If phase conductor was broken then
1. Disconnect 1 of the phase/line conductors out of circuit breaker
2. Test all sockets and note which ones have no reading and what the socket/sockets with highest Zs values.... Ermm just thinking about misleading values from spurs
3. Disconnect this leg and then do the same again with the other leg connected.
4. Hopefully should then give good idea of where the break is.
However can you elaborate on this please:)