Confused - lighting circuit.

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Liam Regan

New member
Joined
Nov 24, 2024
Messages
2
Reaction score
0
Hello, any help will be appreciated. One of the RCDs tripped that protected the downstairs lights, kitchen and upstairs sockets. Process of elimination showed the issue to be with the downstairs lights. At the time it tripped the two kitchen lights had been on for sometime. Separate switches for them. I switched the hall light on and about 5 minutes later the circuit tripped.

I assumed it would be the hall light that was the issue. One switch two lights. I disconnected both ceiling roses. Went to switch the circuit back on and it tripped again.

I have had problems with the hall lights about two months ago that I thought I resolved. Why suddenly go now?

One by one I disconnected every ceiling light. The circuit still trips.

Am I missing an elephant in the room or is it time to call an expert.
Most of the ceiling roses have connectors as per image. Not like the ones i see in guide videos.
 

Attachments

  • IMG_20241124_120136.jpg
    IMG_20241124_120136.jpg
    4.6 MB
Unfortunately random time RCD trips can be hard to diagnose. The fault doesn't even have to be on the same circuit, because adjacent circuits on the same RCD can interact depending on overall circuit loading.
Hence looking at the last item to be switched is no indication at all if it was several minutes ago.
It could be a faulty appliance on the ring circuit.
You probably need help.
 
Unfortunately random time RCD trips can be hard to diagnose. The fault doesn't even have to be on the same circuit, because adjacent circuits on the same RCD can interact depending on overall circuit loading.
Hence looking at the last item to be switched is no indication at all if it was several minutes ago.
It could be a faulty appliance on the ring circuit.
You probably need help.
Thanks for your quick reply. Of note when i switched the lighting circuit back on, which immediately tripped, there was nothing else on in the house other than usual stand by stuff. Could it still be surrounding circuits.
 
You did say it tripped a few minutes after switch on. If it goes immediately then it's more likely where the fault lies, but still not 100%.
I'll try to explain; When you switch on a load the current drawn slightly raises the potential on the neutral, due to the resistance of the cable. That small potential is applied to all the neutrals which share that RCD. Note that neutrals are not switched by normal MCBs.
Now if one of those dormant circuits has a short, or partial short, to earth, some current will flow and that may be enough to cause the RCD to trip.
An electrician has equipment which can measure for any such short circuit and will quite likely disconnect individual circuits at your consumer unit in order to test them.
 
Hello, any help will be appreciated. One of the RCDs tripped that protected the downstairs lights, kitchen and upstairs sockets. Process of elimination showed the issue to be with the downstairs lights.

Am I missing an elephant in the room or is it time to call an expert.
Most of the ceiling roses have connectors as per image. Not like the ones i see in guide videos.


Unless you have physically disconnected all of the neutrals inside the consumer unit from the every other circuit that shares the same RCD, during your testing of the lighting circuits then you have eliminated nothing.

By the sounds of it, the elephant in the room appears to be that you have not done any formal testing with suitable meters/testers etc. to check insulation resistance, RCD operation etc.??

If the "guide videos" you have been watching don't show you how to to proper dead circuit testing when investigating a fault, or mention what test equipment you need, then they are probably not the best quality instruction guides to follow..?
(I have seen far too many wanna-be video celebrities producing very dubious electrical guidance!)

You fault could just as easily be on a dodgy socket.. or a faulty appliance still plugged in...
As the current from the lights can travel to the common neutrals at the CU, and back out of the CU along a neutral, into a socket, then into the back of a faulty appliance that has a path to earth from its internal neutral wiring. This cant happen it you have disconnected the shared neutrals.

A faulty appliance/socket with a single pole switch does not need to be turned on to allow electricity from a different circuit that shares the same RCD, to cause the RCD to operate.

This is why current wiring regulations do not recommend shared RCD's in domestic dwelling. Although they are electrically safe, they can be quite inconvenient in the event of faults.
 
Top