Hi
I'm looking to install a new induction hob rated at 10.8kw that I calculate at circa 46 amps. I can get a new cable from consumer unit to hob location (approx 3m run) and have a spare slot on consumer unit. I Have the following questions:
1. Can I apply diversity to this type of hob thereby giving a current rating of approx 21amps and allowing me to use 6mm cable and a 32A breaker or do I ignore diversity and go for a higher breaker / 10mm cable?
2. Do I need to use RCD side of consumer unit or none-RCD side? The way I understand things is that if I connect hob using a combined 45A cooker switch / socket I use the RCD side but if I use just a cooker switch only without the socket, I can use the non-RCD side? ( my spared slot on the CU is on the non-RCD side)
many thanks
I'm looking to install a new induction hob rated at 10.8kw that I calculate at circa 46 amps. I can get a new cable from consumer unit to hob location (approx 3m run) and have a spare slot on consumer unit. I Have the following questions:
1. Can I apply diversity to this type of hob thereby giving a current rating of approx 21amps and allowing me to use 6mm cable and a 32A breaker or do I ignore diversity and go for a higher breaker / 10mm cable?
2. Do I need to use RCD side of consumer unit or none-RCD side? The way I understand things is that if I connect hob using a combined 45A cooker switch / socket I use the RCD side but if I use just a cooker switch only without the socket, I can use the non-RCD side? ( my spared slot on the CU is on the non-RCD side)