Oh OK then ... I don't want to enter the glanding civil discussion .
I do not have a choice as this house is to be used for multiple ocupancy and the owner wants the cellar closed to residents but the cu accessable to all. If I move it to the party wall then the tails will go over 3 meter's and need the switched fuse which then is in the cellar with no access. Also there is the potental that the load could go over 80 amps at times so another reason for not using the switched fuse @ 80 amp. The only other idea I can come up with is to mount recessed cu in the party wall at a lower level and build a slim cuboard around it. That would then leave the tails short enough.I don't want to enter the glanding argument, but have you considered how weak the 4" wall will be after you have chased out for the SWA or 32mm steel conduit ( which I see as totally OTT) TBH . I would not even consider chasing a sub main into a 4" wall TBH .
So they are basically saying its not been installed to their instructions if its not glanded.Single Point Bonding of CablesThe current ratings provided by the IEE Wiring Regulations are based on the armour being solidly bonded i.e. earthed at both ends (neither end is left floating). The scenario you describe suggests the cable has been installed with the armour bonded only at one end.
Am i being dumb here but how do you get lid off with an armoured cable connected to it?all insulated c/u i garage with armoured gland and shroud on supply to new pond circuit, (none rcd sub main i might add ; ) )
On the basis of that then DNOs fail to terminate their supply cables correctly (No Glands used)How are you complying with 522.6.1 if you do not use a gland to connect it to the CU (and don't say using cleats as they are unassociated with the CU)?Also:
So they are basically saying its not been installed to their instructions if its not glanded.
because batty bat my friend :^O its a wylex nh type board, nh type mcbs, and the back half and front half of cu are seperate, the armoured and gland arrangment is terminated i the rear half of the c/uAm i being dumb here but how do you get lid off with an armoured cable connected to it?
Sorry its late was thinking the lid was a whole thing forgot they are in two parts.because batty bat my friend :^O its a wylex nh type board, nh type mcbs, and the back half and front half of cu are seperate, the armoured and gland arrangment is terminated i the rear half of the c/u
all is forgiven batty bat :^O :^O :^OSorry its late was thinking the lid was a whole thing forgot they are in two parts. :z
522.6.1How are you complying with 522.6.1 if you do not use a gland to connect it to the CU (and don't say using cleats as they are unassociated with the CU)?
Thats up to the DNO but 7671 requires us to follow manufacturers instructions.On the basis of that then DNOs fail to terminate their supply cables correctly (No Glands used)Also are we failing to comply with Manufacturer by segregating SWA feeds to Outbuildings by only Terminating Armour one end?
They are very good. I can highly recommend them.Couldn't you use one of those dooberries that clamp onto the armour?http://www.tlc-direct.co.uk/Main_Index/Earthing_Index/Piranhna_Earth_Nuts/index.html
Found it...
T&E is not as heavy or likely to be subject to so much force. By not using a gland you are not minimising the damage arising from mechanical stress so are not following 522.6.1.522.6.1Wiring systems shall be selected and erected so as to minimize the damage arising from mechanical stress, e.g. by impact, penetration, tension or compression during installation, use or maintenance.
And what keeps a T&E in place when it is brought into a CU? Clips? Trunking? All of which are unassociated with the CU as is a cleat, but you agree they're acceptable? All that reg states is that a cable must be suitable for it's environment not that it has to be glanded.
As for your quote, well I can't argue that and so therefore I won't As I said, if you can put forward evidence I'll accept it.
:Applaud :Applaud:ApplaudI think you are just talking crap now and you should stop being a cowboy and terminate swa into glands.
Well that's one way to end a discussion isn't it?I think you are just talking crap now and you should stop being a cowboy and terminate swa into glands.
But later on you quote this:I would not class that as good workmanship. Should be properly glanded both ends with the CU one potentially being a nylon gland and Earthed at the cut out end.
For your information I do gland SWA's at both ends, but that's my preference. Someone else suggested glanding at one end and although I would gland it at both ends, I didn't see any reason why his method was not valid.Also:
Originally Posted by Cable manufacturer
Single Point Bonding of Cables
The current ratings provided by the IEE Wiring Regulations are based on the armour being solidly bonded i.e. earthed at both ends (neither end is left floating). The scenario you describe suggests the cable has been installed with the armour bonded only at one end.
So they are basically saying its not been installed to their instructions if its not glanded.