Not sure if FP is allowed. Pyro yes.also, shouldnt central battery systems be wired in pyro / FP?
It seems that there is only 1 type of fitting with 1 circuit in it so it runs on AC under normal conditions and DC in a power failure.Of course this will only work if the emergency circuit in the lights will run on AC.
Assuming you mean kA, not kV.it's an old fashiouned centralised emergency battery system - I've only ever seen the remains of 1, far easier as said above to do away with it.
As for 6kV MCBs, the fact the incoming is 10kV is irrelevent, the individual ccts protected by individual MCBs and related maximum fault currents of those ccts is what actually matters. ie MCBs protect what's downstream of them, and that PFC is what relates to the 6kV rating. This subject has been discussed on here before.
However, a UPS is a different animal to a central battery system.In some areas UPS systems are the only thing allowed to meet the required protection.
Nope the max PFC for the cct is just after the MCB, to get near 6Ka, you need to dead short the cct about 1mm after the MCB to get almost zero resistance - generally physically impossibleAssuming you mean kA, not kV.
The maximum fault current for the circuit will be the PFC at the DB (or near enough) if the fault occurs close to the DB.
Of course yes - The battery is a centralised unit - No local batteries!It seems that there is only 1 type of fitting with 1 circuit in it so it runs on AC under normal conditions and DC in a power failure.
OK, take a real-world example.Nope the max PFC for the cct is just after the MCB, to get near 6Ka, you need to dead short the cct about 1mm after the MCB to get almost zero resistance - generally physically impossible