Disconnection time 120 volts Uo vs 150 volts Uo

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

ProMbrooke

Active member
Joined
Nov 23, 2019
Messages
36
Reaction score
0
Is there any real danger in using a 0.8 seconds as disconnection time for 150 volts line to ground? Or would a sweet spot at 0.7 seconds work? Call me cheap but I don't want to use 0.4 seconds unless I really have to.
 

 
well table 41.1 requires 0.4 for TN or 0.2 for TT (both AC), so if you want to deviate then you would have to justify that and mark it int he deviations box on your EIC/MWC

 
But is there really any danger Andy? I don't see a huge increase in danger between 120 and 150 volts line to ground.

Switch on

listen

nothing?

jog on

bang?

get someone in

jog on




Lets stick to electrical theory here please :)

 
But is there really any danger Andy? I don't see a huge increase in danger between 120 and 150 volts line to ground.

Lets stick to electrical theory here please :)
Oh I think you would be unpleasantly surprised at the number of people who subscribe to the aforementioned testing procedure 

 
OK, in the UK on building sites we use a lot of 110V tools, which gives an RMS value of 50V ish. 50v is regarded as a 'safe' touch voltage, under fault conditions. Clearly the higher the voltage the more risk people are at, but how much difference say an extra 10V adds I don't know. 

 
True, but remember that in place like the Republic of the Philippines, Saudi Arabia and South America power is distributed line to line. So its 127 to 138 volts line to ground.

 
UK regs are based off of IEC-60364. Same disconnection time is in the IEC. My question is- does a 0.8 second disconnect time really pose any hazard at 150 volts to ground? If so would a 0.65 second timing be ok? 0.4 seems like extra material.

 
I'm trying to remeber what the disconnection times were before it all went 0.4?  We suppossedly work on 230V which is roughly 115V to ground and certainly hurts! 

 
I'd be curious to know. 138 volts is 69 volts to remote earth so I'm not that concerned going over 0.4 seconds.

 
OK, in the UK on building sites we use a lot of 110V tools, which gives an RMS value of 50V ish. 50v is regarded as a 'safe' touch voltage, under fault conditions. Clearly the higher the voltage the more risk people are at, but how much difference say an extra 10V adds I don't know. 


but 110v site supplies are 55v to earth single phase, 63.5v 3 phase. not his 150v to earth

 