120V or 230V to earth is the norm throughout the world. I'm not sure about Outer Mongolia.
likewise, sounds like foreign places to me
120V or 230V to earth is the norm throughout the world. I'm not sure about Outer Mongolia.
Firstly with faults. It is the U0 Voltage that we are concerned with.
How are you determining the disconnection time, is this a theoretical exercise, a design or calculation, or is it a measured value which when compare to the breaker impedance is giving these disconnection times?
At the instant of the fault the supply live conductor and the protective conductor act as a voltage divider.
To simplify things, lets allow them to be of equal value for a moment, this means at the instant of fault you are dropping half U0 in the line & half U0 in the protective conductor.
The exact values will vary depending on the exact impedances, but for this model 50:50 will do.
So, with U0=120V this gives 60V at the point of the fault, with U0=150V you have 75V.
From this you can look back at the tables and data in IEC 61140 & IEC 61479 and derive the allowable disconnection times.
These times are related to the physiology of the body, expected heart rate, body impedance etc. For the population based on statistical models.
120V or 230V to earth is the norm throughout the world. I'm not sure about Outer Mongolia.
Do I think it's a good idea to stretch the disconnection time, no, would I recommend it or say that it is acceptable, never.
Nope I have to disagree with that statement.Yes, but remember that it means more copper. Having to run 4mm2 where 2.5mm2 will do is a big incentive to use a longer disconnect time.
Yes, but remember that it means more copper. Having to run 4mm2 where 2.5mm2 will do is a big incentive to use a longer disconnect time.
so are you happy to possibly kill people to save money?
Nope I have to disagree with that statement.
If it was perhaps 2.5 mm sq. instead of 195mm sq. perhaps, but the specific difference in cost between 2.5 & 4 is negligible.
The difference is that it's not the actual voltage that is considered in this under IEC requirements nut the nominal one.
Thus the voltage divisor is already allowed for in IEC considerations.
basically use a longer disconnection time to save a few £ in cable...
Thats why I'm referencing the IEC's body graph and asking here. 0.8 to 0.4 is a big jump.
I know the IEC us using a voltage divider, and that the nominal voltage can be +10%.
However, 0.8 seconds for a 120 volt Uo and 0.4 seconds for a 138 volt Uo is a big jump. Why not 0.75 or 0.6 at most?
Cost adds up in big projects not to mention its harder to work with and terminate 4mm2 on a socket terminal.
Normally the volt drop gets you way before the loop impedance anyway, especially since the limits were tightened up.
I'm confused, where does this say 75 volts for 0.8 seconds at a tpyical body impedance results in burns or ventricular fibrillation?