Thats pretty much what I read in the OSG this is what I finally came up with (sorry its long)
Maximum demand for the whole installation
Using Table 1B in Appendix 1 On Site Guide
DB1 Circuit No. Ib After diversity
L1 L2 L3
Ring Final Circuit DB1 L1 1 32A 32A
Ring Final Circuit DB1 L2 1 32A 16A
Lighting Circuit DB1 L3 1 4.3A 3.9A
Lighting Circuit DB1 L3 2 4.3A 3.9A
Lighting Circuit DB1 L3 3 4.9A 4.4A
Lighting Circuit DB1 L3 4 2.2A 2.0A
Lighting Circuit DB1 L3 5 5.1A 4.6A
DB2 Circuit No. Ib After diversity
L1 L2 L3
Ring Final Circuit DB2 L1 1 32A 32A
Ring Final Circuit DB2 L3 1 32A 16A
Lighting Circuit DB2 L2 1 5.8A 5.2A
Lighting Circuit DB2 L2 2 3.7A 3.3A
Lighting Circuit DB2 L2 3 3.7A 3.3A
Lighting Circuit DB2 L2 4 3.7A 3.3A
Lighting Circuit DB2 L1 2 2.2A 2.0A
Lighting Circuit DB2 L3 2 5.2A 4.7A
DB3 Circuit No. Ib After diversity
L1 L2 L3
Ring Final Circuit DB3 L2 1 32A 32A
Radial Circuit DB3 L1 1 20A 10A
Lighting Circuit DB3 L3 1 3.4A 3.1A
Hand Drier DB3 L1 2 3.9A 3.9A
Lighting Circuit DB3 L3 2 4.3A 3.9A
Lighting Circuit DB3 L3 3 4.9A 4.4A
Lighting Circuit DB3 L3 4 4.9A 4.4A
Lighting Circuit DB3 L3 5 2.9A 2.6A
DB4 Circuit No. Ib After diversity
L1 L2 L3
Ring Final Circuit DB4 L2 1 32A 32A
Ring Final Circuit DB4 L1 1 32A 16A
Fridges DB4 L3 1 10.4A 10.4A
Cooker DB4 L2 2 18.3 18.3A
Coffee machine DB4 L2 3 11.7A 11.7A
Dishwasher DB4 L3 2 18.3 18.3A
Lighting Circuit DB4 L1 3 2.9A 2.6A
Lighting Circuit DB4 L2 4 3.5A 3.2A
Lighting Circuit DB4 L3 3 2.9A 2.6A
Lighting Circuit DB4 L3 4 2.9A 2.6A
Lighting Circuit DB4 L3 5 2.2A 2.0A
DB5 Circuit No. Ib After diversity
L1 L2 L3
Ring Final Circuit DB5 L1 1 32A 32A
Hand driers DB5 L2 1 7.8A 7.8A
Hand Driers DB5 L3 1 7.8A 7.8A
Lighting Circuit DB5 L2 2 1.8A 1.6A
Lighting Circuit DB5 L2 3 1.8A 1.6A
Lighting Circuit DB5 L3 2 4.9A 4.4A
Lighting Circuit DB5 L3 3 4.9A 4.4A
Lighting Circuit DB5 L3 4 4.9A 4.4A
Lighting Circuit DB5 L2 4 4.4A 4.0A
HVAC HVAC 63A 63A 63A 63A
LIFT LIFT 63A 63A 63A 63A
Total Maximum demand on installation 256.5A 237.3A 240.8A
What do you think?