Went round to a house today to price for a new triton electric shower replacement as the old one has given up, done the usual walk round and noticed no Earth connected to the TNS Head ( No bond onto SWA )
looked at the water main next to it Bonded ok but plastic pipe running into the ground so no earth, checked the gas No Bond I can see maybe under the boards !!
House built in 1934
Got the old Fluke out and measured the Ze, 0.14ohms, 16th edition RCD with 6 MCB's no Main earth ever fitted.
So advised customer to call DNO, they said there's not a lot they can do so the husband phoned up instead and he is now getting somebody to come out and have a look.
The thing is if you find a BS951 fitted to it and call it in they just come and change it, but if it never had an earth then it's like asking for a blow-job off the pope.
What's everybody else's experience with this situation!!!!