It was probably a term devised by rcd & cu manufacturers in conjunction with the IEE to make the sparky spend more money on equipment to sell to the poor un-suspecting customer!!
Just stating this for the learners on the forum.Amongst others Batty, but in general not domestic dwellings at this stage.
sometime, when I get a chance, (and I dont know just when ATM), although I have a load of other stuff going on just now,Steps,The thing is IF you have complied with 7671, then it is EXTREMELY doubtful that you would ever end up in front of the coroner as you have a robust defence already provided and endorsed by HSE & the LA's, i.e. 7671!
I do understand where you are coming from, and I agree with you, totally!
My disagreement comes from the requirement to comply with 7671, you cannot "fail" an install on personal opinion on a PIR, I wish we could.
If you put an observation on a PIR you must be able to back that up with a Reg. No. which gives the non compliance and, I have not been able to find "that" reg. no.
To have an issue with a single pole solid neutral RCBO even on a TT would require more than 1 fault/defect, does 7671 allow for multiple simultaneous faults each of which creates a cascade effect to a more dangerous situation...
---------- Post Auto-Merged at 22:45 ---------- Previous post was made at 22:44 ----------
Canoe,
Shame I'm not with ELECSA as I would have turned the inspector grey!
Ok forgive my use of the phrase nuisance tripping ! i just imagined water had gotten into my system somehow and the blasted RCD had tripped. If i were on holiday that would be a nuisance . lolOr the new fangled word for energising RCD protected circuits without prior testing for any shared neutrals or low insulation resistances due to damaged cables. Nuisance tripping would be a faulty oversensitive RCD, which should be easily rectified by replacing the faulty RCD, after checking all the standard operating trip times and preferable with a ramp test as well. Doc H