This is one of those typical situations where you need to apply more than a 5WW training concept of X=good and Y=bad....
When looking at the results of a Ze or Ra test on a TT installation,
a bit of understanding of the ground conditions your rod(s) is/are sunk into needs to be considered..
Some things BS7671 related do NOT fit into easy tick-box, or idiot guide flow charts...
Earth rods is one of them IMHO..
you need to be able to apply your full understanding of the reg's and what safety considerations you are aiming to achieve..
and the practical limitations of the geography of your installations..
In certain situations on three different site locations 56ohm, 134ohm, 205ohm, may all be perfectly reasonable and good Ze values..
that are all impossible to achieve at the other sites, or different time of year..
due to the soil/ground types..
Single, Extended or Multiple rods / Sandy, Clay, Rocky ground etc..
tested during a really dry or damp period of weather can have significant effects of what you can or can't achieve for your Ra & thus Ze...
So it you don't take full account of the conditions of your earth arrangements when assessing if your test readings are acceptable or not..
you could end up tying yourself in knots trying to achieve the impossible..
I know some places round here that are very sandy and you can push a 1m rod in by hand , others where after 4inches you need to use a mallet or hammer drill to bang a rod in..
If you want a bit of bedtime reading...
https://www.weschler.com/wp-content/uploads/2020/01/gettingdowntoearth.pdf
When you have read that....
Come back and we will test you...
correction...
come back and you can test us!!!