You might want to confirm that you have 'continuity' where there should be continuity - and Insulation Resistance where there should be Insulation Resistance.....................before the plasterers come in and board it all.
Also, a true R1 + R2 measurement is a measurement of the resistance of the 'Line' conductor (R1) added to the resistance of the CPC (R2).
You might think I'm stating the obvious here, but what I mean is it is ONLY R1 + R2 - nothing else...............it shouldn't include things like earthed 'exposed conductive parts' - for example steel conduit or cable tray (unless specifically designed as the CPC for the circuit), so the measurement would be taken before 2nd fix, before all the little 'flyleads' etc are connected up - otherwise, why bother measuring it at all?
Calculating Zs will tell you that your 'disconnection times'
should or
shouldn't be met -
measuring Zs will tell you that they
will or they
won't........a huge difference, and that
is a fact.