hi

I have just bought a tester cheep but when i do the earth loop test it trips the rcd. the only lead i have for doing the test is one with a plug.

how do I do the test?

thanks

craig

 

patspark

Senior Member
Joined
Mar 26, 2008
Messages
243
Reaction score
0
Location
London
as steptoe said give us a clue what tester have you got my tester has one a setting witch will not trip the rcd you may have the same d lock more info

needed

 
Joined
Feb 14, 2008
Messages
7,480
Reaction score
21
Location
Cloud Cuckoo Land
My old Robin earth loop has 'D Lock' to prevent the Rcd tripping. This works by saturating the Rcd coil with DC. Modern Rcbo's can sense both AC & DC ( largely because lots of new PSU'S can put out DC when working, preventing an Rcd from tripping) I can not use this on Rcbo's and have bought a fluke multi tester now.

Why did you think your meter was cheap ?

 

daryl631

Member
Joined
Feb 26, 2008
Messages
65
Reaction score
0
had same problem with alphatec meter using plug changed to using different plug adapter and it worked ok

 

davetheglitz

Electrician
Joined
Mar 18, 2008
Messages
822
Reaction score
1
Location
Saltash, Cornwall
Some older meters were not designed for use with an RCD - probably why it was cheap (I bought an old Metrotest a couple of years ago before I realised this!). Other than buying a new meter the easiest way round this is by calculation. Use the meter to measure Ze at source - no RCD problems there, and then use low ohm meter to measure R1 + Rs (apply short at one end and measure at the other - don't forget to remove the short!) Zs = Ze + R1 + R2.

 
Joined
Mar 7, 2008
Messages
9,994
Reaction score
0
Location
In the office again.
Also any electrical equipment plugged into circuit gets fried 25 amp current does that.batty
EH????

The "25A" which is so vaunted about, is a pulse on a half - cycle; between phase and earth. Unless the item connected has a functional earth connection ( which you`ve already fried with your insulation test (which chucks more voltage down the line than things were designed to handle.) - it isn`t a problem. 25A is NOT flowing through any connected equipment m8. Common misconception.

 
Joined
Feb 27, 2008
Messages
11,034
Reaction score
0
Just going by a job i did years ago doing a loop test on a circuit that an electrician had connected a shed into. client was asked to take all appliances out of sockets on circuit. She had said all sockets were empty. Got a call back a next day to say stereo would not work turned out that fuse had blown.

batty

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,337
Reaction score
117
Location
Gtr Manchester
EH????The "25A" which is so vaunted about, is a pulse on a half - cycle; between phase and earth. Unless the item connected has a functional earth connection ( which you`ve already fried with your insulation test (which chucks more voltage down the line than things were designed to handle.) - it isn`t a problem. 25A is NOT flowing through any connected equipment m8. Common misconception.
thanks KME Ive been sitting here trying to work this out, never heard of it before except in faulty equipment(which as you say would already fry on IR!)

or in certain industrial, which aint very common either TBH, and I think at that stage people doing that work understand how it works.

;)

 

dougal

Well-known member
Joined
May 13, 2008
Messages
178
Reaction score
0
the tester is a seaward sbs7671

I can do the short circuit test but not the earth loop

to do the test at the moment uses a "kettle lead"

there is an option to buy another lead that has the "kettle" plug at one end and three probes on the other But this retails at

 
Joined
Feb 27, 2008
Messages
11,034
Reaction score
0
I was talking about Robin loop testers with d-lok the small yellow ones. These test at 25 amp for a short period. I don't use mine anymore. I use Di-log 9083p. These test at a lot lower amperage.

batty

 

extension15

Distinguished Member
Joined
Feb 13, 2008
Messages
1,659
Reaction score
0
I was talking about Robin loop testers with d-lok the small yellow ones. These test at 25 amp for a short period. I don't use mine anymore. I use Di-log 9083p. These test at a lot lower amperage.batty
And there you are then...

Technology improves......

]:)

 