Tried that You have to link the neutral out as well.or link out the L at the RCD :O]
EH????Also any electrical equipment plugged into circuit gets fried 25 amp current does that.batty
thanks KME Ive been sitting here trying to work this out, never heard of it before except in faulty equipment(which as you say would already fry on IR!)EH????The "25A" which is so vaunted about, is a pulse on a half - cycle; between phase and earth. Unless the item connected has a functional earth connection ( which you`ve already fried with your insulation test (which chucks more voltage down the line than things were designed to handle.) - it isn`t a problem. 25A is NOT flowing through any connected equipment m8. Common misconception.
the tester is a seaward sbs7671I can do the short circuit test but not the earth loop
to do the test at the moment uses a "kettle lead"
there is an option to buy another lead that has the "kettle" plug at one end and three probes on the other But this retails at
And there you are then...I was talking about Robin loop testers with d-lok the small yellow ones. These test at 25 amp for a short period. I don't use mine anymore. I use Di-log 9083p. These test at a lot lower amperage.batty