Kind of.They 'rod' (for want of a better word), the supply neutral, which gives you the PME supply.
The operative word is Protective Multiple Earthing - multiple simply means
more than one - so they could 'rod' the supply twice or ten times.....it's still PME (I think this is Steptoes grievance with PME
)
Now, if your house had a TNS earthing system before they convert their supply neutral, it will still be a TNS earthing system after they convert their supply - the TNS applies to the earthing system provided to the installation, not what the supply is capable of providing.
Think of it this way - If we took Steptoes advice and converted all TNCS (PME) installs to TT, then the installations would be TT, regardless of the fact that the supply neutral is still a PEN conductor with PME supply.
In the same way your installation is still TNS, until such time as the DNO allow connection of your 'earthing conductor' to the neutral, then it becomes TNCS.