Earthing

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

spacebiscuit

Member
Joined
Jan 2, 2025
Messages
5
Reaction score
0
Location
UK
I'm thinking I should earth down my PV on my flat roof. Can I use 6mm cable - the 10mm seems like it will be hard to work with but I believe is what regs state. Would 6mm do anything in the event of say a lightening strike. My thinking is that 6mm is better than nothing at all?

Other question - does it have to earth down to a rod in the ground or can I tie it into the house somewhere which is already earthed down?

For the record I have retrofitted my panels myself, I'm not sure that they were previously earthed down.
 
Nothing will protect you from a direct lightning strike, so I wouldn't worry about that.
I'll let more knowledgeable members comment on the need for any earthing, (bonding?) but I know my professionally installed system has none.
 
there was never a requirement to earth PV, except under some odd circumstances which I wont go into. Adding an earth bond may actually attract a lighting strike - easier path the earth. The only thing an earth bond does offer is easier fault finding in the event of an insulation fault with the array.
 
I'm thinking I should earth down my PV on my flat roof. Can I use 6mm cable - the 10mm seems like it will be hard to work with but I believe is what regs state. Would 6mm do anything in the event of say a lightening strike. My thinking is that 6mm is better than nothing at all?

Other question - does it have to earth down to a rod in the ground or can I tie it into the house somewhere which is already earthed down?

For the record I have retrofitted my panels myself, I'm not sure that they were previously earthed down.

Which are the regs you are referring to that suggest a 10mm is required for a lightening conductor??
 
there was never a requirement to earth PV, except under some odd circumstances which I wont go into. Adding an earth bond may actually attract a lighting strike - easier path the earth. The only thing an earth bond does offer is easier fault finding in the event of an insulation fault with the array.
I think the bit about "attracting a lightning strike" has been disproved now. But you are right that domestic PV is not generally earthed.
 
If you have enphase micro. Inverters which operate at reduce dc voltage on the array as per solar panel is a Seperate inverter underneath is there any other things re earthing that is needed to be done as the voltage on the solar pv will be a max of around 60 ish volts dc not several hundreds in dc volts
 
Lightning protection as I was told many years ago by a guy in the techinal dept of a large well known lightning protection manufacturer is a dark art where doing nothing can be safer than installing a lightning protection system that could be more dangerous if a strike occurred

I'm thinking I should earth down my PV on my flat roof. Can I use 6mm cable - the 10mm seems like it will be hard to work with but I believe is what regs state. Would 6mm do anything in the event of say a lightening strike. My thinking is that 6mm is better than nothing at all?

Other question - does it have to earth down to a rod in the ground or can I tie it into the house somewhere which is already earthed down?

For the record I have retrofitted my panels myself, I'm not sure that they were previously earthed down.
Given that the down lead / conductor on a lightning protection system is normally a 25 x 3mm copper tape (75mm² CSA) I think 6 or 10mm² might be somewhat under sized for the task.
I would suggest unless you have a good understanding of lightning protection and the placing of earth rods to minimise the risk of the step potentials that may occur during a lightning strike then my advice would be to leave well alone
 