Question>>
A transformer is rated at 10kW but is only delivering 9.8kW. Copper losses are 0.33kW and Iron losses are 0.2kW. Calculate the efficiency of the transformer.
98%
99%
90.4%
88.6%
My calculation..
Efficiency = output/input X 100
therefore 9.8 / 10.53 ( this includes the losses 0.2+0.33 ) x 100
I have the answer of 93%
>>>>> I hope my calculation is right, if not , can anyone show me the right one please..
thank you all..
Lplate
The question is worded to throw you off the cent , (I believe) , your formula is correct but you have thrown the information that isnt relavent into it .
See if you can work it out from that information.