Rob_the_rich
Sock Muncher
- Joined
- Mar 2, 2010
- Messages
- 1,343
- Reaction score
- 27
yes, effectivelyso you are effectively saying a fault could be effectively by passing the cpc by using the neutral instead. I see your point.
yes, effectivelyso you are effectively saying a fault could be effectively by passing the cpc by using the neutral instead. I see your point.
I was thinking all the time , this a N to E fault ( Honestly ) but were unable to do any tracing .It is, or should be, a ring circuit, so if you plug the tester anywhere in the ring, some of the cpc current will be going down the neutral, as above, wherever the fault is in the ring. At x1 rated current of rcd, instead of 30mA going down the cpc, some will divert to the neutral, so the rcd sees maybe 15mA, enough not to trip.
Depending on the load the same thing happens, where high protective conductor currents occur, the rcd might not see any imbalance.
This is what I was thinking but we couldn't get on with it .This is a combination of a loose connection on the neutral and a squashed core in a back box, don't ask me to explain it but I have come across it before, had to pull every front and checked terminals one loose, tested fault had disappeared.
Dave , we meggered the outgoing legs when we had some sockets off , that was OK , but needed to pull the plug on the fridge. Meanwhile the old dear was mythering about the plugs being off the wall and will they be level when you put them back.What were the IR tests?
If the customer won't allow you to investigate a fault, then you can only note the fault on the EICR and code it.
I always prefer to try and find faults and would prefer to fix a simple fault and give it a satisfactory than have to code it and quote for remedial work, but if the customer does not want you to do that, then you can't force them.
Was the occupier, the "customer" or is she the tenant?
She thought the PIR would take 1/2 hour.
We had the kitchen ring with high trip time for the RCBO the rest of the place was fine .
Trip time was 300mS , plus the tester dithered slightly , the two LED lights flicker, go dim then it trips.
Tried a second RCD tester ( Yes we are two tester firm) That flashed up reading of 7 which immediately faded , followed by "ERROR 5 " :C
Thinking its a faulty RCBO I swap with the next breaker but the same occurs, so wiring fault .
Readings were R1 = .22 / Rn = .38 / R2 = .43 / R1 + R2 = .69 Zs .3
We started checking ( not being paid for that) but there was a socket behind a built in fridge , for the fridge, old dear wouldn't let us remove the fridge ....." I should get the kitchen fitters back they will know how to remove it ." ( Two screws) Then didn't really want us to return to sort it so what do you do?
There,s something wrong somewhere but we've had to leave it .
The other trip times were :-
12
12
9
12
12
8
300
7.8
:C
It seems to be a common belief in fairness. When you explain you will need a few hours some people seem dumbfounded by this! Probably why they expect it to cost about £50!What made her think that?
Have you just added r1 to r2 to give you the (R1+R2), or is this a spur? Because otherwise it should be around about 0.16 Ohms.Readings were R1 = .22 / Rn = .38 / R2 = .43 / R1 + R2 = .69 Zs .3
If she is Greek,shouldn't she be getting a German in to fix it for free?She's an 80 yr old Greek woman Murdo . I don't know why she imagined that , like many people , has no idea about how long things take .
You're right there , I jotted the readings on a bit of paper ..... r1 + r2 is .69 R1 & R2 on my cert copy was .17It seems to be a common belief in fairness. When you explain you will need a few hours some people seem dumbfounded by this! Probably why they expect it to cost about £50!
Have you just added r1 to r2 to give you the (R1+R2), or is this a spur? Because otherwise it should be around about 0.16 Ohms.