Just had mine (didn't want to tell you all first incase I didn't pass).
Well as I am telling you know, you can guess that I did pass. Had 2 observations.
1) Had to downgrade a fuse on a distribution circuit (as it was 30A protecting a 2.5mm cable), so now one of the mcb's in the remote board was much higher (20A & 32A) so didn't allow for discrimination. I had already sourced the CCU with the 32A in so left it as I am planning on replacing distribution with 4 or 6mm in the future.
2) I admitted to him I hadn't removed the bonds (or turned off the power) when I did the Ze test (should have kept quiet) so he got me to do it now.
Other than that he seemed happy. Apparently ELECSA have lots of people in Worthing.
Ian.
Well as I am telling you know, you can guess that I did pass. Had 2 observations.
1) Had to downgrade a fuse on a distribution circuit (as it was 30A protecting a 2.5mm cable), so now one of the mcb's in the remote board was much higher (20A & 32A) so didn't allow for discrimination. I had already sourced the CCU with the 32A in so left it as I am planning on replacing distribution with 4 or 6mm in the future.