If 3 hr min duration  fittings are installed, should they be tested to 3hrs if the application only needs 1 hr duration. If a 3hr fitting fails in  say 80min  where only 1 hour is needed what would you put on the cert. 

I have only once seen a 1 hour duration emg light, they all seem to be 3 hr now.

 
Last edited by a moderator:
There are many views on this, high risk area emergency lighting is probably the only type of emergency lighting where a definition of the time required to maintain the light is mentioned. Basically it says that it has to "kick in" within 0.5 seconds and maintain 10% of the normal lighting for as long as the hazard requires to be safely shut down.

So if it takes 5 minutes to shut down a machine for example then the requirement is that the light should remain on for at least that length of time.

Now in the test procedures we have to do a full 3 hour run down to test the battery packs for say open area lighting and fail those that do not achieve the full 3 hours. I have just tested a building where the fire plan and evacuation is around two minutes, in my view as long as people are evacuated safely I really do not see the problem. However it is not my call so I fail all those that do not achieve the full 3 hour run down.

 