hi thanks to all the guys who advised on my forthcoming initial niceic inspection in respect to my replacing my father in laws consumer unit. The information offered was of great help leaving just the question of what i should fill in on the eic. i.e everything or ????cheers in anticipation chrisgjudd
p.s is the nic good for public liability or can another party be recommended???? ]
Hello M8
Fundimental rule to remember IS..
If you have changed a CU..
every circuits charactereistic have been changed.
& most likely they have a different fuse protection device which has a different max permited Zs and possibly different current ratings??
e.g.
5A BS3036 now 6A BSEN60898
15A BS3036 now 16A BSEN60898
30A BS3036 now 32A BSEN60898
Larger meter tails & main earth conductor would also have implication on the actual Zs reading.
You must prove that you have reconnected the circuits correctly, no high res joints & correct polarity etc..
With regard to Insulation resistance it is often impractical to completely dissconnect everything from a circuit to check all combinations of IR test.
It can be permissable to check with L&N joined together with referencxe to earth 'CPC' conductor. and put 'LIM' in boxes for L-N test.
You inspector will need to see you reperform some of these tests and check your readings!
so try and find an easily accessible / isolatable radial circuit...
such as a cooker with socket outlet can be a good one!
SL.