Right here goes , I see yet another reference to exporting the earth from a PME supply ( TNCS) to a remote building etc. My question is , can someone tell me which Regulation covers this . I have to admit that prior to becoming a Forumite I had not come across this, and still cannot see why it is a problem.PME means Permament Mutiple Earthing , the neutral is spiked to earth along it's run and seperated where it enters a building, so its a reliable connection to earth. TNCS is the new name but nothing has changed, the earth and neutral are combined in the supply and seperated on entering the building.
A sub supply to a remote garage or shed , say, would be classed as TNS, or should I be donning Spec's big pants on my head.
Deke if you go back to post #9 on this thread
http://www.talk.electricianforum.co.uk/showthread.php?t=4409
where I was explain to AndyC that one site can have multiple installations
the Regulations that govern whether you can or cannot export your PME earth are noted.
i.e. Requirements for protective conductors between installations with separate earth arrangements
Regulation 542.1.8 page 126
Where a number of installations have separate earthing arrangements, any protective conductors common to any of these installations shall either be capable of carrying the maximum fault current likely to flow through them or be earthed within one installation only and insulated from the earthing arrangements of any other installation. In the latter circumstances, if the protective conductor forms part of a cable, the protective conductor shall be earthed only in the installation containing the associated protective device.
So if you had a PME & TT joined together i.e. two earth types are present and the connected earth protective conductor MUST be able to carry full fault current.. so if faulty broken neutral at PME end then the earth via the TT rod becomes the neutral path for the whole installation so would need to be 25mmCSA assuming live is 25mmCSA!
The basic requirements for protective earthing from reg 411.3.1.1 page 46.
state that Exposed conductive parts must be connected to a protective conductor and simultaneously accessible parts MUST be connected to the same earth system.
SO referring to the two above points..
Exposed-conductive-parts connected to two earthing arrangements must not be simultaneously accessible.
If such parts could be accessed simultaneously, a physical barrier, physical separation or a non-conducting enclosure must be provided to prevent this.
If the outbuilding has exposed conductive parts AND a single earth system is used e.g. PME exported from house, those exposed parts would be connected back to the PME at the house so the earth conductor MUST have a big enough CSA.
REMEMBER EXPOSED CONDUCTIVE PARTS ARE THOSE THAT INTRODUCE AN EARTH POTENTIAL. e.g. metal pipes, structural steel into foundations etc..
IF the outbuilding has NO exposed conductive parts & thus no introduced low resistance earth path then the PME can be exported.
e.g. total wooden shed on support battens with no pipework entering the shed...
This will meet BOTH of the above regs so OK exported.
Obviously if the house supply was TT or TNS the max fault current down the earth conductor would NEVER be the full load current. e.g. a broken neutral in these situations would just mean NO power! :|
so only a smaller CSA earth needed to safely export earth.