Went to look at a job today. I only went to look at an outside light that was faulty. It's turned into so much more.... Potentially!
At the meter cupboard the tails go into Henley blocks where they split to the house and to a small 2 way dB with a 30mA rcd up front. 16mm 3 core armoured is glanded into this but no banjo to earth the armour.
That 3 core then goes underground to a external large garage with a flat above. The armoured hasn't been glanded at this end at all. The DB is a 16th 10 way split board .
From this DB the flat above is fed with a 16mm twin and earth and another 16 mm swa goes to a indoor swimming pool which is also another separate building. The pool isn't heated but does have a sauna.
I haven't fully checked the pool installation for compliance to the regs.
The swa from the 16th board to the pool building was done in the last couple of years and signed off part p.
My first concern was the exported earth, and the armour from the meter cupboard not being earthed at one end and the other end having no gland at all.
My proposal is to disconnect the earth out of the swa that comes from the meter box and put an earth spike protecting the garage DB which in turn then puts the pool building protected by the spike too. Gland the armoured at the garage end and earth the armour from there.
Any further pearls of wisdom for me please? Or perhaps I'm over doing it?
At the meter cupboard the tails go into Henley blocks where they split to the house and to a small 2 way dB with a 30mA rcd up front. 16mm 3 core armoured is glanded into this but no banjo to earth the armour.
That 3 core then goes underground to a external large garage with a flat above. The armoured hasn't been glanded at this end at all. The DB is a 16th 10 way split board .
From this DB the flat above is fed with a 16mm twin and earth and another 16 mm swa goes to a indoor swimming pool which is also another separate building. The pool isn't heated but does have a sauna.
I haven't fully checked the pool installation for compliance to the regs.
The swa from the 16th board to the pool building was done in the last couple of years and signed off part p.
My first concern was the exported earth, and the armour from the meter cupboard not being earthed at one end and the other end having no gland at all.
My proposal is to disconnect the earth out of the swa that comes from the meter box and put an earth spike protecting the garage DB which in turn then puts the pool building protected by the spike too. Gland the armoured at the garage end and earth the armour from there.
Any further pearls of wisdom for me please? Or perhaps I'm over doing it?