Has anyone had the chance to work on relocating a CU and extending the meter tails? It looks like the new tails will need to be 6-8m long to satisfy the customers request. How did you go about this task if you've experienced this sort of job?
This question has been categorically answered by Sidney in one fell swoop and needs no embellishment . In my 'umble opinion of course.
One would have to choose an installation method that does not trigger a need for RCD protection of the tails.Not sure that I 100% agree with that .................. surely the installation method of the "new tails" might lead to 1 or 2 additional questions and answers ....................
I believe the general DNO approach is that <=3m is acceptable, though quite often long tails are installed in new builds and different DNOs may have different standards I am sure one of them has 4m as the maximum length.Is there a reg associated with keeping the tails less than 3m, or is it just accepted practice? Sorry, what I'm saying I guess is, what are we trying to fulfil by doing so?
One would have to choose an installation method that does not trigger a need for RCD protection of the tails.
most DNOs stipulated meter tails up to 3 mtrs long could be protected by their cut-out fuse . Longer than 3M a sw/fuse should be fitted to discriminate over theirs .