Hello MartyJ, welcome to the forum. Are there any other openings in the room such as vents or windows. If the room has no other openings, is the fan operating correctly with a suitable duration of run-on timer? (building reg's recommend 15minutes). How long is the ducting before the vent reaches outside? Many people have a fan that is only on while they are in the room that then goes off immediately they leave. This will not have sufficient time to remove residual moist air / steam so will promote mould growth etc. Also to extract air out, there must be an equivalent vent size letting air come into the room. (otherwise the fan is trying to create a vacuum.) Typically with an enclosed room this requires a 10mm gap under the bottom of the average 760mm door to allow a standard 100mm diameter extractor vent pipe to pull in the same volume of air. Again many people have plush fitted carpets in the adjoin room so there is no inlet ventilation to the en-suit. (a simple test to check the gap is can you poke you fingers under the en-suit door from both sides?). Providing you have appropriate inlet ventilation, adequate timer run-on and the extract duct is not several meters long though the loft void, then the fan should do the job. It looks like a Greenwood Airvac to me? But if there are several metres of duct to reach the outside it would be better with a higher power in-line centrifugal fan.
Doc H.