Hi All
Wondered if anyone had any opinions on this one, I did a Periodic yesterday on a smallish unit, which was part of a whole estate, it had a three phase 100 amp supply split off via henley blocks into one wylex (addition) and on merlin Gerin (original installation) dis boards. ZE at both baords was coming up as 0.01ohms giving me a PEFC of 19.8 KA and PSCC Measured from Line to Neutral of 19.9 KA, Doubled because they are both three phase gets me up to nearly 40Ka.
The breaking Current of the MCB's is 10Ka and 9Ka for the merlin stuff and 6KA for the Wylex. I am puzzled that the instalation is 18 years old and had numerous additions, that in fairness are of a high quality, but this has never been flagged. Also what would you guys offer as a cost effective solution.
Russell
Wondered if anyone had any opinions on this one, I did a Periodic yesterday on a smallish unit, which was part of a whole estate, it had a three phase 100 amp supply split off via henley blocks into one wylex (addition) and on merlin Gerin (original installation) dis boards. ZE at both baords was coming up as 0.01ohms giving me a PEFC of 19.8 KA and PSCC Measured from Line to Neutral of 19.9 KA, Doubled because they are both three phase gets me up to nearly 40Ka.
The breaking Current of the MCB's is 10Ka and 9Ka for the merlin stuff and 6KA for the Wylex. I am puzzled that the instalation is 18 years old and had numerous additions, that in fairness are of a high quality, but this has never been flagged. Also what would you guys offer as a cost effective solution.