afternoon, just had a total block headbang so can some one just steer me in the right direction.
installed some outdoor lights with 1.5mm2 3 core SWA which is fed from a SFCU (3a) off the downstairs ring main. on the MWC in part 2 is the "overcurrent protected device for the modified circuit" the 32a 60898 or the 3a 1362. and if its the 3a 1362 would the max disc time be 5s or 0.4s (looking at table 41.4 in BRB and getting confused) the circuit is protected by rcd in main consumer unit.
thanks in advance
wayne
installed some outdoor lights with 1.5mm2 3 core SWA which is fed from a SFCU (3a) off the downstairs ring main. on the MWC in part 2 is the "overcurrent protected device for the modified circuit" the 32a 60898 or the 3a 1362. and if its the 3a 1362 would the max disc time be 5s or 0.4s (looking at table 41.4 in BRB and getting confused) the circuit is protected by rcd in main consumer unit.