I have been maintaining & modifying a fire alarm system at a 'care in the community' type house (its not classed as a residential care home, although thats what it is) for many years. There are many things wrong that i always include on the quarterly report, but the system works and is maintained. Some of the non compliances are
The supply wired in pvc/pvc
System not zoned properly (should be divided up more)
Some detectors too near light fittings
No visual beacons
Main panel in middle of building, not near any external door or window (due to extensions)
Some detection zones wired in pvc/pvc ( allowed at the time)
Call points not directly by exit doors due to building alterations
Its a standard conventional 4 zone panel, 2 bell circuits system and the panel now needs replacing. This time they have listened to me and agreed to move the panel to the entrance lobby & renew the feed. A few questions
1) If i move the position and fit a replacement panel, as long as i list what is still 'wrong' am i off the hook or am i liable for the whole system
2) Easiest way to do this is to extend the cables in 2 x 7c FP cable. If i mix zones & bells in these 2 cables is this allowed under BS5839, obviously everything will be fire rated its the running the zones together i cant find any reference to. Its no different to singles in trunking and conduit in my eyes
3) At least one detector zone is wired in twin & earth pvc/pvc. Is this ok to leave (once again is a fire alarm certification similar to BS7671 where as long as you indicate what you have done and signing for , your covered)
I am looking into fitting the replacement panel in the same position and fitting a repeater by the front door, but do the points above still stand
awaiting your answers eagerly
The supply wired in pvc/pvc
System not zoned properly (should be divided up more)
Some detectors too near light fittings
No visual beacons
Main panel in middle of building, not near any external door or window (due to extensions)
Some detection zones wired in pvc/pvc ( allowed at the time)
Call points not directly by exit doors due to building alterations
Its a standard conventional 4 zone panel, 2 bell circuits system and the panel now needs replacing. This time they have listened to me and agreed to move the panel to the entrance lobby & renew the feed. A few questions
1) If i move the position and fit a replacement panel, as long as i list what is still 'wrong' am i off the hook or am i liable for the whole system
2) Easiest way to do this is to extend the cables in 2 x 7c FP cable. If i mix zones & bells in these 2 cables is this allowed under BS5839, obviously everything will be fire rated its the running the zones together i cant find any reference to. Its no different to singles in trunking and conduit in my eyes
3) At least one detector zone is wired in twin & earth pvc/pvc. Is this ok to leave (once again is a fire alarm certification similar to BS7671 where as long as you indicate what you have done and signing for , your covered)
I am looking into fitting the replacement panel in the same position and fitting a repeater by the front door, but do the points above still stand
awaiting your answers eagerly