Like the exaggeration!you could hang 2000000000000000 sockets off a spur and they could all draw 13A without the fuses going and thats like 26000000000000000A so the wire will melt but at least the delorian will get its 1.21 gigawatts. If its a fused spur then the fuse int eh spur will go before the wire melts and you will never get back tot he future.(numbers deliberately exaggerated)
Ian.
Possibly not before the cable had melted and set fire to the house. Most ring mains are protected at 32A and wired in 2.5mm that has a max rating of 27A (at best) so as you can see the cable is already over rated before the overcurrent device disconnects the supply.Like the exaggeration! If the spur wasn't fused though and loads of sockets were taken from the spur then surely the MCB would trip in the event of an overcurrent?
3 Questions Ian:Possibly not before the cable had melted and set fire to the house. Most ring mains are protected at 32A and wired in 2.5mm that has a max rating of 27A (at best) so as you can see the cable is already over rated before the overcurrent device disconnects the supply.Ian.
my red3 Questions Ian:1) In a ring main, if one of the legs is broken, the other leg will then have to take the full load i.e. potentially 32A on a cable only capable of taking 27A. Isn't this dangerous?
yes, its dangerous
2) Can spurs be taken off radial circuits? If so am I right in saying they wouldn't need to be fused as the cable rating would be higher that the MCB?
you can add another branch to a radial at any point. you can also take another branch from that branch at any point. providing all wiring is same CSA, and complies with max length. you can also use a 2.5 on a 4mm radial but only to feed one socket (same as a ring)
3) Am I right in saying the more the appliances on a circuit = the lower the overall resistance of the circuit = the higher the overall current?the more appliance switched on, the lower the resistance, and the more current that will flow
It's not really a spur if it's on a radial. As long as the cable is correctly rated you can run cables to anywhere from anywhere on the circuit.2) Can spurs be taken off radial circuits? If so am I right in saying they wouldn't need to be fused as the cable rating would be higher that the MCB?
my redThanks Andy. Final questions about the above points:For 1) Wouldn't it be safer to avoid using ring mains for this reason?yes. but as i said in another thread, a fault on L or N is noticed immediately, but a fault on the earth wont be. at least with a ring, you have 2 earth paths
For 2) So the spurs could be non-fused as the MCB provides adequate overcurrent protection?
all wiring is rated above what OPD is, so no problem with adding anything to anywhere
For 3) Does this apply to parallel circuits only?ohms law appliance to anything. the apliance has a resistance, so current will flow through circuit to that. current will also flow to the other appliances on the circuit
If the fused spur is used as a means of isolation supplying 1 x socket outlet wired in 2.5mm T+E for an appliance, as the socket outlet is not easily available or accessible for example, then a 20amp D.P. switch may be used as the means of isolation also, as the maximum current drawn at the socket outlet by the connected appliance will be limited by the fuse fitted in the plugtop.I wonder if someone could clarify this for me. With regards a fused spur - Why does it need to be fused if the plug itself contains a 13A fuse?
I know series connections aren't used but I was just curious to know the answer.Not sure what you're asking exactly. In a standard electrical installation appliances will be in parallel. No series connections will be used.So your question is, if I'm reading it right, null and void.