thats what i was going to suggest, feed bathroom light/fan from spur then loop the 3c/e through a 3 pole isolator.fit a fcu on bathroom light supply then fit a 3 pole isolator next to it above bathroom door. job done
thats what i was going to suggest, feed bathroom light/fan from spur then loop the 3c/e through a 3 pole isolator.fit a fcu on bathroom light supply then fit a 3 pole isolator next to it above bathroom door. job done
Then choose a different manufacturer that does not stipulate a 3A fuse.Clearly the 3A fuse for fans is a nonsense, however the Regulations require adherence to manufacturers' instructions. Therefore to certify that an installation complies with BS7671 then the fan must be fused down if required by the manufacturer.
It is actually normal practice to have lower rating fuses protecting many items of electrical equipment, rather than just the circuit fuses. This aids with discrimination in the event of faults, so it is hardly nonsense.Clearly the 3A fuse for fans is a nonsense.
A 3A 1362 fuse won't discriminate with a 5A 1361 fuse surely?It is actually normal practice to have lower rating fuses protecting many items of electrical equipment, rather than just the circuit fuses. This aids with discrimination in the event of faults, so it is hardly nonsense.Doc H.
That would be one solution.Then choose a different manufacturer that does not stipulate a 3A fuse.
can you point me in the direction of some?Then choose a different manufacturer that does not stipulate a 3A fuse.