If there is already a 17th edition CU there and there are spare ways then I would be tempted to :-
i) Fit a 32A MCB into the exisitng CU,
ii) Install a metalclad adaptable box next to the 17th edition CU,
iii) Run a 6mm 2 core SWA to the garage from the adaptable box,
iv) Install 6mm tails from the adaptable box to the CU, using an earth ring and crimped lug to take a 6mm earth back to the main earth bar,
v) Fit a 4 way CU in the garage (allowing 2 extra ways in case of future additions) containing your 16A and 6A MCB's protected by a main 30ma double pole RCD.
vi) Exporting TNCS to outbuildings is becoming an increasingly controversial issue ! IMHO because the earth and neutral are connected together at the origin and if the neutral is lost and extraneous conductive parts are not reliably connected to the MET then metalwork could become live. I personally would be inclined to terminate the SWA into an insulated enclosure, not taking the earth into the garage CU and fitting an earth rod for the garage, running your earthing conductor from the earth rod to the earth bar of the new garage CU and ensuring the Ra is < 200 ohms. Other members of this forum may suggest exporting the TNCS, uncle Steps will not...
....