So does this rule also apply to a sub mains in a commercial or industrial nature or is this purely a domestic issue only
....either way' date=' even if there was no submain and a neutral failure on DNO side, then neutral & earth will become live[/quote']
On the one occasion I have witnessed that happening, local earth did indeed become "live" (my neon screwdriver illuminated when touched to the MET!!!) but there was enough return path via bonded water and gas pipes to allow enough current to pass to dimly illuminate a couple of lights in the house.
So the bonding of gas and water limited just how much the MET floated upwards, which is the whole point of the "multiple" bit of PME I wish now I had tried to measure just how much "earth" had floated upwards, but as soon as I realised it was enough to light my neon screwdriver, I switched off and called the DNO.
You have to ask which is more dangerous: everything floating upwards (pipes bonded) or "earth" floating upwards but local pipework not (no bonding in place)
But that's a separate topic. The DNO tell us neutral failure in PME is rare, but as I say, I've witnessed it once. Think about this. A split outer sheath of a burried concentric will allow water in to the outer cores, and slowly allow them to corrode. So logic says a ruptured outer core of a concentric must be many many more times more likely than a ruptured inner core.
And what earthing arrangement would that be? As Andy mentioned above, isolate the incoming earth at the cu.If you do export the earth from a pme to the garage can you add an additional TT earth rod and connect to the pme earth in the garage db?
If you exported tn-c-s then yes but then again, why did you not fit a plastic one?I added power to my garage the only conductive part in the garage is the db housing, so this could become live if the neutral is lost from the cu in the house?
Who's Earth are you trying to export?So u can fit a swa to a garage on a tncs system providing no bonding is needed in there and a PVC cu is fitted otherwise if bonding is required then it needs making tt at the garage end in simple terms is this acceptable. Y is it we are having to make are life harder just because of the dnos chances that a neutral will fail in my opinion they should take actions so that never fails