Hello,
I have got myself confused with testing a generator installation.
The generator is A 100kVA 650Vac single phase machine.
The generator is bonded down to true earth via two 16mm - 4ft earth electrodes, and then bonded to the neutral star point of the machine. to create a TNS.
The output is then fed via two 50mm^2 cables to a large stationary metal building. on the side of the building there is a large 10kVA commando type socket rated at 10kVA and 154 Amps, that is then connected to a 650V, 160A MCCB.
The unit is bonded down to true earth via four 16mm earth electrodes.
Inside the unit there are a number of consumer units all with RCBO type b's fitted to every final circuit.
All the normal tests on each board have been carried out an all fall within the normal parameters and Zs disconnection times for the type of RCBO
As the generator is over 10kVA the manufacturer has recommended the neutral be bonded to true earth.
Do i take the zs reading for TNS as 0.80 and then divide into the 650V to give a fault current of 813A
I have measured the Ze as 0.48, and that was with two earth electrodes, with a fault current of 1354A, more than enough to trip the over current MCCB device.
But for the building do i need to test the earth electrodes ?
David
I have got myself confused with testing a generator installation.
The generator is A 100kVA 650Vac single phase machine.
The generator is bonded down to true earth via two 16mm - 4ft earth electrodes, and then bonded to the neutral star point of the machine. to create a TNS.
The output is then fed via two 50mm^2 cables to a large stationary metal building. on the side of the building there is a large 10kVA commando type socket rated at 10kVA and 154 Amps, that is then connected to a 650V, 160A MCCB.
The unit is bonded down to true earth via four 16mm earth electrodes.
Inside the unit there are a number of consumer units all with RCBO type b's fitted to every final circuit.
All the normal tests on each board have been carried out an all fall within the normal parameters and Zs disconnection times for the type of RCBO
As the generator is over 10kVA the manufacturer has recommended the neutral be bonded to true earth.
Do i take the zs reading for TNS as 0.80 and then divide into the 650V to give a fault current of 813A
I have measured the Ze as 0.48, and that was with two earth electrodes, with a fault current of 1354A, more than enough to trip the over current MCCB device.
But for the building do i need to test the earth electrodes ?
David