Hi all so I generally carry out domestic works and small commercial works and now I’m going for my assessment for commercial works 3phase with NICEIC .

now I have found a small new job which I can use for my assessment but need to make sure I get everything spot on .

so I’m ok with all circuit cables etc but here’s something I haven’t yet had to do before .

unit has a 3 phase supply coming into it and electric supply com Sony has requested meter tails be installed from supply to meter location prior to there visit and also meter tails from meter location to distribution board .

now developers of the new site have stated 125kva minimum , 

but having only done domestic 25mm before I’m not sure what size meter tails to come from supply side to meter and from meter to distribution Board based on 125kva ,  as stated this is 3 phase retail shop .

Can someone help?

 
probably getting a 200a service head for that. probably going to need 70 or 95mm for the tails

fit a schneider KQ board, there designed for 250a as standard, just make sure you use a 250a switch and not a 125a

 
Well this is where I’m confused as to be fair the customer only has 3 phase circuit going in the rest are just lights and sockets and a couple of spare ways for anything additional in the future so no massive spec , but the supplier has written this on the supply 

8BB815FA-F0AE-4787-86DB-855B63D087F7.jpeg

switch10 said:
Well this is where I’m confused as to be fair the customer only has 1 x 3 phase circuit going in the rest are just lights and sockets and a couple of spare ways for anything additional in the future so no massive spec , but the supplier has written this on the supply 

8BB815FA-F0AE-4787-86DB-855B63D087F7.jpeg
 So would you say that’s 200amp per phase would you say from what they have written on there? 

 
Well this is where I’m confused as to be fair the customer only has 3 phase circuit going in the rest are just lights and sockets and a couple of spare ways for anything additional in the future so no massive spec , but the supplier has written this on the supply 

View attachment 11566


id expect they will be fitting a meter to the side of that with CT coils around the conductors coming into the top. a bit 100x100 galv trunking on top of that then into your DB would work well

 
probably getting a 200a service head for that. probably going to need 70 or 95mm for the tails

fit a schneider KQ board, there designed for 250a as standard, just make sure you use a 250a switch and not a 125a
Yes this is the board I’ve purchased along with the 250a disconnector add on for board . 
 

just tails that’s puzzling me as will only be in a short length of 100x 100 galv trunking I’m wondering weather to go with 70mm or 90mm tails 

 
and what does table 4D1A say for the current capacity of 70 & 95mm for your reference method?
Well would have to be 95mm as will be enclosed in trunking - but round here we have big problems with meter companies saying they can’t terminate into meters with that size cable , so just worried I install 95mm which is expensive then they come along and won’t connect to meter Because they say cables to big 

 
Last edited by a moderator:
Well would have to be 95mm as will be enclosed in trunking - but round here we have big problems with meter companies saying they can’t terminate into meters with that size cable , so just worried I install 95mm which is expensive then they come along and won’t connect to meter Because they say cables to big 
image.png

this may help

 
we have big problems with meter companies saying they can’t terminate into meters with that size cable ,
but are you not having CTs Fitted ,the tails through the CT into the head ,and the CT connects to the meter using a smaller cable (normally 1.5 or 2.5)

 
but are you not having CTs Fitted ,the tails through the CT into the head ,and the CT connects to the meter using a smaller cable (normally 1.5 or 2.5)
 All I’ve been asked to do is to supply and install tails into the service head - and for these to be terminated before meter installation date - that’s the exact details I’ve got from customer 

 