I wired a shower last week and went back to connect it up and test today, however on testing the Zs of the circuit i get a reading of 0.93ohms, and the MCB maximum is 0.92ohms (50amp Type B) in regs, on the back of my NICEIC test books its 80% which allows 0.73ohms.
More detail, what I have is a Sub Main supplied in 16mm Twin and Earth from a 60amp switch fuse. I have install new 4 way enclosure with 63amp RCD 50amp MCB (shower) 16amp (1x Double skt).
At the top of the RCD i get 0.22ohms, socket is 0.44ohms and the high reading for the shower. Everything else tests ok, my R1+R2 was 0.46ohms. Now i know i could have done my Zs by calculation and would have had a satisfactory result but why is my R1+R2 ok but high Zs.
What are my options of reducing this, different Type MCB, maybe type 1? What other options do I have?
Thanks in advance.
More detail, what I have is a Sub Main supplied in 16mm Twin and Earth from a 60amp switch fuse. I have install new 4 way enclosure with 63amp RCD 50amp MCB (shower) 16amp (1x Double skt).
At the top of the RCD i get 0.22ohms, socket is 0.44ohms and the high reading for the shower. Everything else tests ok, my R1+R2 was 0.46ohms. Now i know i could have done my Zs by calculation and would have had a satisfactory result but why is my R1+R2 ok but high Zs.
What are my options of reducing this, different Type MCB, maybe type 1? What other options do I have?