Hi Guys Just new on here but thought I would give some news on this problem,
on september last year installed a dual rcd board on february this year 2 mcb's 6 amp wylex started melting and within no time set the board on fire it started dripping on the carpet, set house on fire the board was 12" from gas meter and nearly set the house up, scared the **** out me
so right away I new that there had been more than my company working in the house there was ikea fitting a kitchen etc so I contacted my supplier to see if there had been a problem with these mcb's
because in 28 years doing this job I had never seen this before it was nothing like a slack connection which I knew it was't anyway as the connection onthe terminal and the connection on the buss bar was all that was left of the breaker the rest had gone,
anyway I contacted wylex and within 2 hours a rep was out to pick up the board and I was told I would get a lab report in 2 weeks well I am still waiting on the report,
then kept phoning as I had to rewire most mains supply to circuits and shower circuits etc the place was a mess carpets burnt etc,
so I finally got a manger then I was promised a call 2 weeks ago for my payment nothing so called last week and got another guy after getting sent from pillar to post this guy say's he will help
so hope get my payment soon I have another 48 properties to go to with approx 150 mcb's to change the first 2 boards today was 11 mcb's you do get