It is in fact required by the Regulations that it is connected to the means of Earthing.Imho you should always conduct the IR test with the cpc connected to the cu ....
It is in fact required by the Regulations that it is connected to the means of Earthing.Imho you should always conduct the IR test with the cpc connected to the cu ....
It wasn't the 3rd Amendment. It came in with the 17th from the outset.I got pulled on assessment for disconnecting cpc's. think he said leaving them connected came in in 17th (he maybe even said 3rd ed) I never checked up to previous versions though.
Like the rest of the world has done for decades.Well 18th is calling for an Earth rod to be installed regardless of supply arrangement.
Like the rest of the world has done for decades.
It is in fact required by the Regulations that it is connected to the means of Earthing.
Which lots of people don't seem to realise ....
whats the reg number?
612.3.1 is the reference in GN3
Thanks.
I'd missed the earlier reference to this reg in this thread.....
It was introduced with the 17th Edition. Definitely a sensible change in my opinion.Thanks.
I'd missed the earlier reference to this reg in this thread.....
but in our case, its always been the responsibility of the DNO to maintain the earth (unless TT). now there trying to pass it onto us to maintain their earthing network....Like the rest of the world has done for decades.
IR testing is carried out with the cicuit CPC connected to the means of earthing.
That is in the regs.. came out in the original 17th i believe..
To do otherwise means that all you are doing is testing the cable itself, NOT the actual circuit..
[Was not a young lady killed and an electrician jailed for not finding a fault that would have been revealed by proper testing as is required?? A partition wall or something??]