Hello Thomo27...
I am just going to add my observations onto this thread a bit as-well..
Just been reading through... one or two bits still need confirming bit to open ended and as KME quite rightly said earlier..
for the moment ignore the RCD ("problem")
Verify the ring circuit readings are all acceptable first..
or you will be doin a wee-wee in the wind (as they say!!)
You question the difference between Ins Res on Rings / Radials.
Fundamentally there is no difference, other than that the far end of the circuit comes back to the CU.
When you have done you're tests are ALL of the conductors disconnected from the CU?
i.e. you have two T&E cables loose at the CU, six conductors,
2 x live
2 x neutral
2 x earth.
Personally I would step back and re-test all your readings again..
with cables open as above
1/
verify continuity, L-L, N-N, & E-E.
2/
check there are no parallel paths back to the CU bus-bars.
Switch whole installation OFF (main switch),
with Low Resistance meter
go through and test each of your L, N, E cable ends
for any direct continuity back to the CU L, N & E bus-bars?
do the same again with Ins Res to verify No high res path.
3/
With one end of your ring cable all open circuit, (not touching anything),
with meter still on low resistance scale.. and using other end of ring cable
check for any direct path between, L-E, N-E & L-N.
Then check the above again with Insulation res tester..
EVERY SINGLE ONE OF THE ABOVE TEST READINGS SHOULD BE HIGH OR OFF THE SCALE!!!
Note any low readings and tell us what you got??
I am just going to add my observations onto this thread a bit as-well..
Just been reading through... one or two bits still need confirming bit to open ended and as KME quite rightly said earlier..
for the moment ignore the RCD ("problem")
Verify the ring circuit readings are all acceptable first..
or you will be doin a wee-wee in the wind (as they say!!)
You question the difference between Ins Res on Rings / Radials.
Fundamentally there is no difference, other than that the far end of the circuit comes back to the CU.
When you have done you're tests are ALL of the conductors disconnected from the CU?
i.e. you have two T&E cables loose at the CU, six conductors,
2 x live
2 x neutral
2 x earth.
Personally I would step back and re-test all your readings again..
with cables open as above
1/
verify continuity, L-L, N-N, & E-E.
2/
check there are no parallel paths back to the CU bus-bars.
Switch whole installation OFF (main switch),
with Low Resistance meter
go through and test each of your L, N, E cable ends
for any direct continuity back to the CU L, N & E bus-bars?
do the same again with Ins Res to verify No high res path.
3/
With one end of your ring cable all open circuit, (not touching anything),
with meter still on low resistance scale.. and using other end of ring cable
check for any direct path between, L-E, N-E & L-N.
Then check the above again with Insulation res tester..
EVERY SINGLE ONE OF THE ABOVE TEST READINGS SHOULD BE HIGH OR OFF THE SCALE!!!
Note any low readings and tell us what you got??