er... your supposed to get 000 with leads touching?with both leads connected 000leads seperated 299
The Don would expect a high reading, perhaps 299.if you ir test a short piece of cable say 1mm csa would you get a reading and what should it be assuming the cables good
299MohmIf you IR tested a brand new reel of T&E I would expect to get >299mohms on all the readings....DO NOT CONNECT TOGETHER THE OTHER END
for a new cable, expect a reading higher than your test kit can measureif you ir test a short piece of cable say 1mm csa would you get a reading and what should it be assuming the cables good
your testing the IR, try one clip on brown one on blue but dont join the other end.so the test leads have no resistance
dont forget you also need to test the earthyour testing the IR, try one clip on brown one on blue but dont join the other end.
KME the forum was discussing your absence only the other day, hope you are well and welcome back!!Think O/P confused insul. with cont. testing.........
Sounds like it to me too.Think O/P confused insul. with cont. testing.........