Hi,
Ive been to investigate why customers rcd is tripping intermittantly. It was part of a long list of work. I completed the rest early and had some time to spare so I thought id do a full test of the installation (for practice).
Here are some of the results
TNS with Ze of 0.11/PEFC 2.1kA/PSCC 3.8kA
Main fuse 100A BS1361 Type IIB
1) CU Light & Bell (B10 1.0/1.0)
2) Lights up (B10 1.5/1.0)
3) Lights down (B10 1.5/1.0)
4) BLANK
5) BLANK
6) RCD 80A 30mA
7) Shower (B32 6/2.5)
8) Ring (Whole House) (B32 2.5/1.0)
9) Water Heater (B20 2.5/1.0)
10) Garage (B20 2.5/1.0)
11) Kitchen Sockets (B32 4.0/1.5)
R1's & R2's
1) R2 = 0.32 ohms
2) R2 = 1.26 ohms
3) R2 = 1.37 ohms
4) BLANK
5) BLANK
6) RCD
7) R1+R2 = 0.17 ohms
8) R1+R2 = 0.59 but readings varied from 0.37 to 0.59 ohms?
9) R2 = 0.74 ohms
10) R1+R2 = 0.40 ohms
11) R1+R2 = 0.11 ohms
Global Insulation Resistance
L-E >299MOhms
L-N>299MOhms
N-E 38.2MOhms
Earth Fault Loop Impedance (Zs)
1) 0.14 ohms
2) 0.53 ohms
3) 0.32 ohms
4) BLANK
5) BLANK
6) RCD
7) 0.16 ohms
8) 0.51 ohms
10) 0.55 ohms
11) 0.22 ohms
RCD Test
NO TRIP
(0 Degrees) 80.2ms
(180 Degrees) 39.9ms
(0 Degrees) 6.6ms
(180 Degrees) 12.0ms
10mm Earthing Conductor
6mm Main Protective Bonding Conductors
I didnt have to do the full test but had some tim to spare and need practice so i dont what I could.
Still dont really know why the RCD is tripping but PAT tested a few items as there were quite a few extension leads, multi way adaptors etc.
The 10m extension leads earth continuity was 2.48 ohms / Passed IR test but thats a fail for earth continuity?
Would this be one of the reasons why the RCD is trpping apart from acculmulative earth leakage of 3 laptops and the whole house being on one ring?
Any pointers or advice greatfully received ?
Thanksx five delta n
Matt ut the kettle on
1)
Ive been to investigate why customers rcd is tripping intermittantly. It was part of a long list of work. I completed the rest early and had some time to spare so I thought id do a full test of the installation (for practice).
Here are some of the results
TNS with Ze of 0.11/PEFC 2.1kA/PSCC 3.8kA
Main fuse 100A BS1361 Type IIB
1) CU Light & Bell (B10 1.0/1.0)
2) Lights up (B10 1.5/1.0)
3) Lights down (B10 1.5/1.0)
4) BLANK
5) BLANK
6) RCD 80A 30mA
7) Shower (B32 6/2.5)
8) Ring (Whole House) (B32 2.5/1.0)
9) Water Heater (B20 2.5/1.0)
10) Garage (B20 2.5/1.0)
11) Kitchen Sockets (B32 4.0/1.5)
R1's & R2's
1) R2 = 0.32 ohms
2) R2 = 1.26 ohms
3) R2 = 1.37 ohms
4) BLANK
5) BLANK
6) RCD
7) R1+R2 = 0.17 ohms
8) R1+R2 = 0.59 but readings varied from 0.37 to 0.59 ohms?
9) R2 = 0.74 ohms
10) R1+R2 = 0.40 ohms
11) R1+R2 = 0.11 ohms
Global Insulation Resistance
L-E >299MOhms
L-N>299MOhms
N-E 38.2MOhms
Earth Fault Loop Impedance (Zs)
1) 0.14 ohms
2) 0.53 ohms
3) 0.32 ohms
4) BLANK
5) BLANK
6) RCD
7) 0.16 ohms
8) 0.51 ohms
10) 0.55 ohms
11) 0.22 ohms
RCD Test
10mm Earthing Conductor
6mm Main Protective Bonding Conductors
I didnt have to do the full test but had some tim to spare and need practice so i dont what I could.
Still dont really know why the RCD is tripping but PAT tested a few items as there were quite a few extension leads, multi way adaptors etc.
The 10m extension leads earth continuity was 2.48 ohms / Passed IR test but thats a fail for earth continuity?
Would this be one of the reasons why the RCD is trpping apart from acculmulative earth leakage of 3 laptops and the whole house being on one ring?
Any pointers or advice greatfully received ?
Thanksx five delta n
Matt ut the kettle on
1)