I have been helping my partner's Dad wire up his motorhome.
He has been supplying kit and I've been fitting it.
The van is wired for electric hook up so the site feed comes into a 3 way board protected by an RCD then MCBs to the sockets around the van. There is a cable connecting the van body to the earth terminal in the fusebox.
He also would like an inverter to power the sockets when off grid.
I've fitted a double pole changeover switch between the hook up point on the van and the fusebox so that the inverter if turned on whilst the van is hooked up can't back feed into the site supply.
The inverter he has provided when powered up shows up as no earth (CPC) when tested.
Readings are as follows
L-N 230v
L-E 0v
N-E 0v
Continuity as follows
L-E open circuit
N-E open circuit
E to ground stud of inverter continuity
We've found some instructions for the inverter and it states that it isn't suitable for our intended use. However there is no mention of this grounding stud on the inverter body nor is it shown on the diagram of the inverter.
Questions are,
1.is an inverter like we have dangerous when used in this set up?
2.If we were to bond the ground stud of the inverter to the van body would this make it safe to use in this setup no mention of this ground stud at all in the instructions?
3.Should we only be fitting an inverter that is able to have it's neutral and earth connected, in effect making our own TN-C-S supply from inside the van.
4.I've looked in the blue book under generators and it talks about static converters, is this what they're referring to as an inverter?
He has been supplying kit and I've been fitting it.
The van is wired for electric hook up so the site feed comes into a 3 way board protected by an RCD then MCBs to the sockets around the van. There is a cable connecting the van body to the earth terminal in the fusebox.
He also would like an inverter to power the sockets when off grid.
I've fitted a double pole changeover switch between the hook up point on the van and the fusebox so that the inverter if turned on whilst the van is hooked up can't back feed into the site supply.
The inverter he has provided when powered up shows up as no earth (CPC) when tested.
Readings are as follows
L-N 230v
L-E 0v
N-E 0v
Continuity as follows
L-E open circuit
N-E open circuit
E to ground stud of inverter continuity
We've found some instructions for the inverter and it states that it isn't suitable for our intended use. However there is no mention of this grounding stud on the inverter body nor is it shown on the diagram of the inverter.
Questions are,
1.is an inverter like we have dangerous when used in this set up?
2.If we were to bond the ground stud of the inverter to the van body would this make it safe to use in this setup no mention of this ground stud at all in the instructions?
3.Should we only be fitting an inverter that is able to have it's neutral and earth connected, in effect making our own TN-C-S supply from inside the van.
4.I've looked in the blue book under generators and it talks about static converters, is this what they're referring to as an inverter?