is an rcd a primary device for protection?

Help Support Talk Electrician Forum:

Lee321

Distinguished Member
Joined
Sep 8, 2008
Messages
2,144
Reaction score
0
a property can have no earthing (very old) and rcd will provide protection against direct and indirect contact?

 

Mr Sworld

Electrical Technician
Joined
Mar 21, 2008
Messages
1,152
Reaction score
0
a property can have no earthing (very old) and rcd will provide protection against direct and indirect contact?
No. RCD's are only classed as additional protection (411.3.3).

While lighting circuits without earths can be allowed (with provisions attached) a property with no earths on all other circuits is a re-wire situation. :)

 

dean mac

Member
Joined
Jul 29, 2008
Messages
117
Reaction score
1
Location
england
No. RCD's are only classed as additional protection (411.3.3).While lighting circuits without earths can be allowed (with provisions attached) a property with no earths on all other circuits is a re-wire situation. :)
do u mean as long as the lighting circuit has no metal fittings or switches

 

The Godfather

Retired
Joined
Mar 24, 2008
Messages
1,302
Reaction score
0
No. RCD's are only classed as additional protection (411.3.3).While lighting circuits without earths can be allowed (with provisions attached) a property with no earths on all other circuits is a re-wire situation. :)
The Godfather agrees.

Don

 

Mr Sworld

Electrical Technician
Joined
Mar 21, 2008
Messages
1,152
Reaction score
0
I'm glad. I can sleep easy tonight! :^O

Mind you after getting into work yesterday at 9am, finishing 7am this morning and then back at 2pm this afternoon and I'm still there X( I shall be resting very easily tonight!

 