hi guys
recently upgraded a consumer unit usual tests performed and satisfactory apart from the rcd auto test, this would fail on kitchen and upstairs sockets, now its never failed before so oviously ive been lucky with upgrades no dodgy wiring anywhere.
anyways as this was an empty property i knew i could pop back once id caught up my work i moved onto my next job which was a kitchen rewire with a cu upgrade again, finished this and again tests were fine until rcd auto test on sockets. i have a metrel mi3000 it is due for calibration next month.
so i then tried switching off all mcbs and testing the rcd only, earth probe to earth bar and live and neutral probes into loadside of rcd press test and again x1 read >300ms.
anyone use this tester i know i will get resistance through the coiled plug in tester so thats why i tried testing at the board and providing ive done it correctly then i presume my tester is at fault or a cheaper solution is that iam at fault haha any help guys would be appreciated thank you
recently upgraded a consumer unit usual tests performed and satisfactory apart from the rcd auto test, this would fail on kitchen and upstairs sockets, now its never failed before so oviously ive been lucky with upgrades no dodgy wiring anywhere.
anyways as this was an empty property i knew i could pop back once id caught up my work i moved onto my next job which was a kitchen rewire with a cu upgrade again, finished this and again tests were fine until rcd auto test on sockets. i have a metrel mi3000 it is due for calibration next month.
so i then tried switching off all mcbs and testing the rcd only, earth probe to earth bar and live and neutral probes into loadside of rcd press test and again x1 read >300ms.
anyone use this tester i know i will get resistance through the coiled plug in tester so thats why i tried testing at the board and providing ive done it correctly then i presume my tester is at fault or a cheaper solution is that iam at fault haha any help guys would be appreciated thank you