May I ask where your getting these 50kA MCBs from as that is a mighty big PFC for a distrbution board?http://www.gepowercontrols.com/ex/resources/literature_library/catalogs/residential/downloads/d_pc_modular200_english_07.pdfThe breakers in this GE panel are rated 10kA. Can a cascading fuse be used upstream so that it can be used at the locations where the available short circuit current is 50kA?
I don't quite understand, how you have a supply cable with an available PFC of 50KA supplying a DB that's rated at 30KA?? If what your saying is correct, then someone somewhere has made a real hush at the design stage !!!I mean that the available short circuit at the panel is 50kA. The MCB's are rated 50kA, which is good. But the Panel itself is rated 30kA. Is it acceptable?
I think there's a bit of a difference between MCBs and MCCBs, especially when it comes to breaking capacities!! ...But i think that was probably a typo mistake. haha!!!Siemens do MCCB's much higher than 25kA, have a few at work on the shelf. From memory they are 35 and 50kA
This is basically very similar to the DNOs BS1361 fuses higher KA rating protecting the so called 16KA domestic CU fault level!! Most of which will have 6KA MCBs and RCBOs fitted... Obviously there's a bit more too it than that, but in answer to your question, ....Yes!!!http://www.gepowercontrols.com/ex/resources/literature_library/catalogs/residential/downloads/d_pc_modular200_english_07.pdfThe breakers in this GE panel are rated 10kA. Can a cascading fuse be used upstream so that it can be used at the locations where the available short circuit current is 50kA?
No .... you were right , the OP was talking MCBs, it was Canoeboy that mentioned MCCBs ...lol .... It's Friday mate ...Hae a Beer !!! lol!!Larnacaman,I missed the MCB bit, when the OP was talking about such fault levels I just read MCCB!
Yes the highest rated mcb I can recall is 10kA, perhaps 15 or 16.
The higher ratigns were as you say MCCB's!
Got to day now getting ready for the match...
The LV Switchboard(s) must have cost them an arm and a leg, bracing levels must be around 45+KA. The old rule of thumb when costing switchgear/boards was, ....''For every 5kA over 22KA doubles the bracing costs'' ....Tends to get Expensive!! lol!!Did a 2MVa transformer job a couple of years ago, same factory is having another put in as we speak ( shame i missed out on the latest job though ! )