Good day sparkies,
If I have: [cutout -> meter -> isolator] -> 30mA RCD 5m away -> Henley block shortly after which splits the tails into CU no.1 0.1m away, and CU no.2 10m away. The DNO allows 5m of unprotected (as in switchfuse) meter tails.
Would this be bending the 5m rule by having the RCD at the end of the 5m allowed length rather than the CU? ]
Where should I locate the switchfuse to protect the tails? ?:|
Thank you for your time