wet risers for that height,
Hi Andy, I know that for really high buildings they have wet risers instead of dry ones, but why is that?? I would have thought that a fire engine can pump water to a much higher head than the municipal water mains??
The water is pushed through the base pump (appliance) & up the dry risers at 10 bar.Hi Andy, I know that for really high buildings they have wet risers instead of dry ones, but why is that?? I would have thought that a fire engine can pump water to a much higher head than the municipal water mains??
john..
The appliance connects in to the hydrant (mains) with twin hose lengths & connects to the dry riser inlets, the pump operator then charges the riser when requested.Possibly because of the amount of water and the time needed to get it up to where it is needed? Probably find some larger buildings would empty an engines tanks just priming the line.
An already unstable structure will be made worse with the weight of water sloshing through it.What I never understand in these situations is why people don't just start flooding the place? Given that the electricity would have been cut off??
The appliance connects in to the hydrant (mains) with twin hose lengths & connects to the dry riser inlets, the pump operator then charges the riser when requested.
When I was involved with the fire service, the issue we had with large fires was that there are a number of hydrants connected to the same main, the more pumps you connect the lower the pressure. We had one big job and we effectively robbed all the water that was meant to feed domestic properties. in some area's deemed high risk the hydrants are actually on their own water main, this was fairly common years ago, but due to costs it's now only done in special circumstances.I suppose that makes sense, I'd imagine they have ample mains hydrants specified along with the dry riser so they know they can just bring a pump in and have it connected and working?
pressure drop, same as voltage drop. if you pump 10 bar of water in at ground level then at 50mtr you only have 5 bar at your hoseHi Andy, I know that for really high buildings they have wet risers instead of dry ones, but why is that?? I would have thought that a fire engine can pump water to a much higher head than the municipal water mains??
john..
The reduction in 'separate feed' fire hydrants was due to increased levels of fire safety, allegedly. As for building checks I think it isn't a case of less buildings being checked, more a case of standards slipping, which as we all know seems to be happening in all sectors these days.Sadly on this occasion it has cost lives.LFB, not checing buildings, and insufficient fire mains hydrants. Could that be due to cutting public service funding?
An excellent way of describing it Andy.pressure drop, same as voltage drop. if you pump 10 bar of water in at ground level then at 50mtr you only have 5 bar at your hose
wet risers are not connected to the mains water. they have their own dedicated tanks and pumps
wet risers are not connected to the mains water. they have their own dedicated tanks and pumps
The FH and WO come from the old days when there were separate mains, Water pumped into the main marked FH or fire hydrant, wasn't treated and as such unsuitable for drinking. The other one WO, water outlet, could be used for drinking as it was fed off the potable water main.We used to use hydrants occasionally when doing drain work, the brigade never objected as we'd report faulty hydrants as we found them, now however it's down to the water authority and all standpipes have to have meters fitted to them, you must have a licence to take water from a hydrant and the meter on the standpipe is read and you are billed at regular intervals.depends on the hydrant iirc, if its marked FH then its the fire brigades responsibility, if its marked WO then its the water board. if you have a stand pipe then you can only legally use those marked WO