I've been on site this week and had the opportunity to watch some subbed in sparks running cabling for a 3-phase changeover switch. The cables in question are each 1x300mm sq single core armoured routed on a tray each with a current carrying capacity of over 600A. They have run 4 cables i.e. 3P+N. I happened to overhear a conversation, something on the lines of "They haven't sent any earths!", and half jokingly asked if they were going to use the armoured. The guy responded on the lines of "What you mean use the banjos?".
Anyway today I see they have NOT run a separate CPC and one of them confirmed they would be using the armoured.
It got me thinking as to whether this is correct and I dug my regs out later. Looking at TABLE 54.8 it suggests a minimum COPPER equivalent CSA for the main protective bonding conductor of 50mm sq where the supply neutral is over 150mm sq (as I said its 300mm sq).
Is it the case then that that the combined CSA of the armoured on all 4 cables that have been run would exceed 50mm sq? I'm guessing it would. Even then, it's not copper I'm thinking.
Good practice, pulling the wool, me missing something etc?
All comments appreciated.
Anyway today I see they have NOT run a separate CPC and one of them confirmed they would be using the armoured.
It got me thinking as to whether this is correct and I dug my regs out later. Looking at TABLE 54.8 it suggests a minimum COPPER equivalent CSA for the main protective bonding conductor of 50mm sq where the supply neutral is over 150mm sq (as I said its 300mm sq).
Is it the case then that that the combined CSA of the armoured on all 4 cables that have been run would exceed 50mm sq? I'm guessing it would. Even then, it's not copper I'm thinking.
Good practice, pulling the wool, me missing something etc?
All comments appreciated.