Megger mft1553
G bizzle
Apr 9, 2018
11
-2
Can anybody tell me what settings and leads to use  with the megger mft1553. On the live testing. Am i right with what ive put?
Pscc      pfc phase+ neutral   phase+ cpc
Pefc       record highest
Ze       disconnect  main cpc
           high loop
           phase + cpc
           red green
Zs      no trip loop
          Phase  cpc neutral
          Red green black
now were getting somewhere but still wrong
for Zs you dont need non trip if there is no RCD. you would only need red & green too
PSCC & PEFC are wrong. re-read PFC, PEFC & PSCC
Pscc  phase+neutral
Pefc   phase+cpc
           PFC Red+green
           Record highest
Ze
           Remove main cpc
           Phase+cpc
           High loop Red+green
Zs
           Rcd protected circuits
           No trip  red green black
           Phase+neural+cpc
           No rcd
           PFC red+green
           Phase+neutral
           Phase+cpc
Megger mft1553 live tests
Ze: remove main cpc
      Test cpc+phase
      Green+red high loop setting
Zs: no trip loop
      End of circuit rcd protected
      Red green black
PFC pfc loop
        Red green black
Ze: remove main cpc
      Test cpc+phase
Zs: no trip loop
      Red green black
PFC pfc loop
        Red green black
A major safety  issue here - although its a   live test the main switch must be off before  removing the main cpc
@G bizzle  it would be useful if you gave us some info about your background in electrics ie are you fully trained, short course trained, are you a DiYer, or are you still training? It would seem, from your posts, you don't have much idea about testing, or at least how to use a multi-function tester. You will get a much better response from the members on here if you are open and honest with us.
Love tests with megger mft1553
Ze  isolate db from incoming supply
Remove main cpc
High loop setting red green leads
Cpc+phase
Record results
Pfc reconnect main cpc
 Red green black leads pfc setting
Test between line neutral + cpc
Record results kA
Zs  Ze+(r1+r2)=zs
Protected circuits by rcd
Red green black leads   no trip loop
Line neutral cpc