Looking at the BRB, at appendix 4, table 4A2 we are given different factors for the various installation methods.
For example method 103 has a factor of .5
Now looking at table 4D5 we are given different current carrying capacities for the various installation methods
EG. 8A for method 103
Should both criteria be applied? I.E. For a 1mm cable ; .5 x 8 = 4A