Why are you using this cable?
You know that unless the accessory termination points are rated to 90dec C you have to de-rate the cable.
This is what was on the design spec. It stated that this cable was used for the dishwasher.
Possibly, that depends on whether those lights would be utilised 100% of the time that the main pool lights were.
Who are you studying with?
TS4U should have covered all this in class for you.
ok, but that's unfair on you, design, is really important.
A dishwasher will be heating the water most of the time during the wash cycle so the maximum load would be drawn at most times when it is in operation.
Therefore the design current is 32A.
Since you have been given that figure it should not be necessary to use any other value.
In other circumstances where you only have the power (in watts) then you would use P/V = I, using the design voltage of 230V.
If you look at appendix 3 of BS7671 the tables beside the graphs give the Ia, minimum disconnection current to use.
For a 6A type B it is 30A as given on page 370.
You are correct with reading the R1+R2 value from table I1: 2.30 mΩ/m for a 16mm² line and cpc.
Tabulated value x length gives the R1+R2 at 20°C in milliohms.
To get the R1+R2 value at maximum normal conductor operating temperature (70°C) multiply by 1.2.
To get the value at 35°C multiply by (1+((35-20)*0.004)) = 1.06
The adiabatic equation is easier if you have the energy let through (I²t) for the protective device as the BS7671 graphs do not go up to the sort of fault levels normally seen.